I am getting "Stack Same path" warning when running Config Advisor. This is because of the connectivity of the primary and redundant path on four stack of FC shelves look like this:
1d, 1c
3d, 3c
11b, 11a
4d, 4c
I guess what this means, is if the module (example IOM on port 1 where 1d and 1c) breaks, then I lose the entire stack, am I right? potential loss of data? especially since we are using software base ownership (disk assign)
I plan to recable them, but I want to learn more, but I plan to recable them like these:
1d, 3c
3d, 11a
11b, 4c
4d, 1c
What will be the best approach on recabling them? Total shutdown? anything else need to be done on the OS level?
Thanks,
md