Parts 1 and 2 covered why bare-metal StorageGRID on FlexPod makes sense and how to actually build it — networks, UCS server profile templates, SAN boot, and the node containers themselves. Once the grid is up, two questions follow immediately: how much capacity and throughput should this design actually deliver, and how do you confirm it's delivering it. This post covers both — sizing the grid's data-protection scheme and per-node resources, and the methodology for validating that the deployment performs as expected before it goes into production.
Size the data-protection scheme first
Before worrying about NICs and CPU cores, the biggest sizing decision in any StorageGRID design is how objects are protected — replication or erasure coding — because it drives both usable capacity and the number of Storage Nodes the grid needs.
- Replication stores full copies of an object on multiple nodes. It's simple and fast, but doubles storage overhead for two copies, and it's the more efficient choice for small objects — roughly 200KB and under — where erasure coding's metadata and compute overhead outweighs its capacity savings.
- Erasure coding (EC) slices an object into k data fragments, computes m parity fragments, and spreads all k+m fragments across Storage Nodes. Any k of them are enough to reconstruct the object, so the grid can lose up to m fragments and stay readable. Storage overhead is simply m/k — a 4+2 scheme costs 50% overhead; 8+2 costs only 25%.
A few of the erasure-coding schemes StorageGRID supports, and what they cost in nodes and capacity:
Scheme (k+m) | Min. sites | Recommended nodes/site | Total nodes | Site-loss protection | Overhead |
|---|
4+2 | 3 | 3 | 9 | Yes | 50% |
6+2 | 4 | 3 | 12 | Yes | 33% |
8+2 | 5 | 3 | 15 | Yes | 25% |
6+3 | 3 | 4 | 12 | Yes | 50% |
2+1 | 3 | 3 | 9 | Yes | 50% |
The rule of thumb: a storage pool needs at least k+m Storage Nodes to use a given scheme, and NetApp recommends k+m+1 so the grid can absorb one temporarily unavailable node without ingest failures or ILM backlogs. Schemes with fewer total fragments (k+m) are generally more efficient — less network traffic to rebuild an object, larger fragment sizes, less metadata overhead — so the usual guidance is to pick the smallest k+m that meets the required fault tolerance and site-protection needs, and to use 4+2 or 6+3 if unsure. Please note that erasure-coding schemes can also be implemented within a single site that has more than the recommended number of total nodes needed for the scheme.
This decision also sets the floor for how many physical hosts the FlexPod build needs — a 6+3 scheme with site protection wants a minimum of 12 Storage Nodes across three sites, which is a very different UCS footprint than the three-host evaluation build in Part 2. For detailed capacity and node-count planning against a specific workload, run the design through NetApp's Fusion sizing tool rather than estimating by hand; what's in this post is the platform-level sizing that sits alongside it.
Then size compute and network per node
With the data-protection scheme and node count settled, the per-node compute and network sizing from Part 2 determines how much throughput each node can actually push:
- CPU and RAM. StorageGRID's 8-core/24GB-per-container minimum is a floor, not a target — Gateway nodes doing TLS termination and load balancing, and Storage Nodes running erasure coding computations, both benefit from headroom above the minimum if the UCS server has cores to spare.
- Network bandwidth. The grid network carries every erasure-coding fragment and every replication copy between Storage Nodes, in addition to client ingest arriving through the client network — so grid-network throughput is usually the first thing to saturate, not CPU. This is where the dual-fabric vNIC design from Part 2 pays off twice: it's redundant, and with both fabric paths healthy it's also the aggregate bandwidth budget for the network the grid depends on most.
- Fabric interconnect and Nexus uplink capacity. Because every StorageGRID network now rides two vNICs pinned across Fabric A and Fabric B, the uplink bandwidth from each fabric interconnect to the Nexus layer needs enough headroom for the aggregate grid, admin, and client traffic from every host on that fabric — not just one host's worth.
Validate: methodology
NetApp's guidance for measuring PUT/GET performance is straightforward, and it applies just as well to a bare-metal grid as to an appliance-based one:
- Test with object sizes that match what the grid will actually ingest — small-object and large-object performance differ substantially, and a benchmark run with the wrong object size profile is not representative.
- Run tests against both local and remote sites if the grid spans more than one.
- Look at both average request latency and overall throughput, not just one or the other.
- Repeat the same tests on a regular cadence and keep the results, so a regression shows up as a trend rather than a surprise.
For load generation, S3tester is an open-source S3 benchmarking tool built specifically for this kind of testing; COSBench is another commonly used S3 load generator for larger, multi-client test scenarios. Independent of either tool, every S3 PUT/GET/HEAD/DELETE operation is timed in StorageGRID's own audit log — the TIME attribute in the SPUT and SGET audit messages gives the grid's own view of request latency, which is useful for cross-checking whatever a client-side tool reports.
What to test on this platform specifically
On top of the general PUT/GET methodology above, a bare-metal-on-FlexPod build has a few things worth checking that are specific to this design:
- Baseline the network before layering S3 traffic on it. Run iperf between hosts across each bonded interface to confirm the grid, admin, and client networks deliver the throughput the UCS vNIC and Nexus VLAN design was sized for — before assuming any shortfall in S3 throughput is StorageGRID's fault rather than the network under it.
- Test PUT/GET throughput per Gateway node and in aggregate. Since client requests load-balance across all Gateway nodes, single-node numbers and aggregate-cluster numbers tell different stories — both matter.
- Pull one fabric on purpose. With each network bonded active-backup across Fabric A and Fabric B, simulate a fabric interconnect failure (or just shut down one uplink) during a sustained PUT/GET test and confirm the bond fails over without the grid reporting node connectivity alarms, and that latency recovers once traffic settles on the surviving fabric.
- Compare against whatever baseline is available. If the organization already runs StorageGRID on an appliance or in VMs elsewhere, running the same S3tester profile against both is the most direct way to validate the performance case for bare-metal made in Part 2 — rather than relying on general expectations about hypervisor overhead.
What's next
With sizing settled and a validation baseline recorded, the next post in this series turns to data protection: using S3 Object Lock and immutable object storage as part of a ransomware-resilient backup strategy. After that, the series closes with the day-2 side — expansion, upgrades, and long-term monitoring of the grid.