Hello Everyone,
I have an old system off support:
Model Name: FAS3240
NetApp Release 8.2.5P5 7-Mode: Thu Jan 7 04:22:14 PST 2021
Suddenly 0a has gone offline:
HA Group Notification from xxxxxxxxxxxx(Write Verification Error: Port 0a Failed) CRITICAL
Fri Jan 21 07:47:07 EST [XXXXXXXX:disk.ioMediumError:warning]: Medium error on disk 0a.13.16: op 0x28:5e53efc4:00fc sector 1582559233 SCSI:medium error - Unrecovered read error - If the disk is in a RAID group, the subsystem will attempt to reconstruct unreadable data (3 11 0 d4) (1728) [NETAPP X302_WVULC01TSSM NA04] S/N [WD-WCAW32566134]
Fri Jan 21 07:47:07 EST [xxxxxxxxxxx:disk.ioReassignSuccess:notice]: disk 0a.13.16: sector 1582559233 was reassigned (140). [NETAPP X302_WVULC01TSSM NA04] S/N [WD-WCAW32566134]
Fri Jan 21 07:47:25 EST [xxxxxxxxxx:disk.checksum.offlineAdapter:error]: Adapter 0a taken offline due to checksum verification failure on multiple disks.
Fri Jan 21 07:47:25 EST [xxxxxxx:callhome.hba.failed:EMERGENCY]: Call home for Write Verification Error: Port 0a Failed
Fri Jan 21 07:47:25 EST [xxxxxxxxx:sas.adapter.offlining:info]: Offlining SAS adapter 0a.
Fri Jan 21 07:47:25 EST [xxxxxxxxxxx:sas.adapter.offline:info]: SAS adapter 0a is now offline.
Fri Jan 21 07:47:25 EST [xxxxxxxxxx:shelf.config.tospha:info]: System has transitioned to single path HA attached storage
slot 0: SAS Host Adapter 0a (PMC-Sierra PM8001 rev. C, SAS, <OFFLINE (soft)>)
Firmware rev: 01.12.09.00
Base WWN: 5:00a098:00353db:b0
Phy State: [0] Disabled
[1] Disabled
[2] Disabled
[3] Disabled
QSFP Vendor: Molex Inc.
QSFP Part Number: 112-00177+A0
QSFP Type: Passive Copper 2m ID:01
QSFP Serial Number: 111620897
I think it relates to the below KB:
I also noticed the following on the shelf attached to 0a:
Possible issue on shelf 10 consider re-seat modules:
Vendor Unique Element 83-IOM3: (SAS)
Element Status Status Bytes Status Descriptions
1 [IOM3 A] : NONCRITICAL 03,0C,00,00 BACKPLANE VPD FAULT, MASTER
2 [IOM3 B] : NONCRITICAL 03,04,00,00 BACKPLANE VPD FAULT
Channel: 4b
Shelf: 10
SES device path: local access: 4b.10.99
Module type: IOM3; monitoring is active
Shelf status: non-critical condition
SES Configuration, shelf 10:
logical identifier=0x50050cc10201fc08
vendor identification=NETAPP
product identification=DS4243
product revision level=0212
Vendor-specific information:
Product Serial Number: SHJ0000000030B1
Status reads attempted: 14550397; failed: 0
Control writes attempted: 0; failed: 0
Shelf bays with disk devices installed:
My thoughts would be to replace the cable from 0a to the shelf and consider re-seating the modules.
Does anyone have any ideas for this ?
Solved! See The Solution
You could try the steps you have planned, nothing to loose. B'cos if it's down to faulty SAS HBA port then it could also mean replacement of motherboard.
Call home for Write Verification Error: Port 0x Failed
https://mysupport.netapp.com/site/article?lang=en&page=%2FAdvice_and_Troubleshooting%2FData_Storage_Systems%2FFAS_Systems%2FCall_home_for_Write_Verifi...
Bug:
https://mysupport.netapp.com/site/bugs-online/product/ONTAP/BURT/708354
As the 8.2 (is still under limited software support) - You could try opening a ticket with support for their opinion (software related only). But, as you are aware, anything related to hardware [FAS3240, EOSH:31-12-18] will need to be addressed outside of support.
You could try the steps you have planned, nothing to loose. B'cos if it's down to faulty SAS HBA port then it could also mean replacement of motherboard.
Call home for Write Verification Error: Port 0x Failed
https://mysupport.netapp.com/site/article?lang=en&page=%2FAdvice_and_Troubleshooting%2FData_Storage_Systems%2FFAS_Systems%2FCall_home_for_Write_Verifi...
Bug:
https://mysupport.netapp.com/site/bugs-online/product/ONTAP/BURT/708354
As the 8.2 (is still under limited software support) - You could try opening a ticket with support for their opinion (software related only). But, as you are aware, anything related to hardware [FAS3240, EOSH:31-12-18] will need to be addressed outside of support.
Thanks so much let me try this