I got a new shelf that i need to add to the netapp. any idea how to do this ?
how   do i put the sas cables in?
1 ACCEPTED SOLUTION
chute
Just to provide one last piece of info on this. TDUBB1234 and I had a discussion offline about disk ownership. The disks are currently owned by node 2, but the option is there to change ownership if need be.
12 REPLIES 12
ryanbeaty
That is a simple question, and at the same time a loaded question. First off, call NetApp support if you are not comfortable doing this. They'll walk you through it.
My post is assuming you are running Multi-path HA.
If this is an HA pair I'd run the following options command on both NetApp controllers...
options disk.auto_assign off
Do not cable the shelf up yet. If the shelf has the same ID as another already running it could cause some issues. NetApp does a good job at keeping same shelf ID's separate, but...
Power on the SAS shelf, set the ID that you want the shelf to be. Usually odds are on controller A and evens on controller B (i.e. fas01-a 10-19, 30-30, etc, while fas01-b 20-29, 40-49, etc.)
After setting the ID on the shelf power the shelf off for 30 seconds. Wait 60 if you want to be sure... It takes some time for the ID to "burn in" and actually set itself.
Power the shelf back on, and add the shelf into the loop. I've stuck to the old school way of A --> D, C --> B. But if you don't know how to install a shelf I've probably lost you already.
Think of the square port as the "Stop" sign. That is where the loop "ends". So from fas01-a port A --> shelf1 Module A square. If you added a second shelf, Module A circle should go to shelf2 Module A square, this then goes to fas01-b port D.
I highly recommend calling NetApp support (you've paid for it might as well use it). Also I recommend reading the setup guide for your particular NetApp controller. It should show you exactly how to configure a single or dual controller configuration (way better than I can describe in words). Log onto the NOW site (now.netapp.com) and click on "Documentaiton -> Product Documentation -> Choose your FAS series -> Installation and Setup Instructions.
This document will show you how the cabling should look like.
Once you get the shelf added, you are going to need to assign the disks to the controller. If you want all disks assigned to one controller (which is recommended) run the "disk assign all" command on that controller. You'll then need to add the disks to the aggregate or create a new aggregate if the disk sizes/speed are different or you've reached your aggregate size limit, but you'll need to calculate the optimal raid group size as well. You don't want a small raid group or you'll run into performance issues.
This does not account for EVERYTHING and all scenarios, which is why it is a simple question but a loaded one.
chute
What type of disk shelf are you trying to add? Information about how to add disk shelves can be found here.
http://support.netapp.com/documentation/productlibrary/index.html?productID=30147
Or, here is the direct link to how to hot add a SAS disk shelf for DS4243, DS2246, and DS4246.
https://library.netapp.com/ecmdocs/ECMP1119629/html/GUID-7272C432-F8FC-4598-BF88-D36173442BD3.html
I would agree with Ryan above and strongly suggest you open a case with NetApp support as a place holder. Be very cautious and thorough if trying this procedure on your own. As always be sure to make any sort of changes within an approved maintenance window and with a supporting change request.
TDUBB1234
how do i find out what disk shelf it is from command line?
chute
For DS42XX - sasadmin expander_map
For DS14MKX - fcadmin device_map
TDUBB1234
this is the result i got
Expanders on channel 0a:
Level 1: WWN 50050cc103124cbf, ID 0, Serial Number ' SHU0954293G1F8R', Product 'DS424IOM3 ', Rev '0132', Slot A
Level 2: WWN 50050cc1028c833f, ID 1, Serial Number ' SHU0954293H17T6', Product 'DS424IOM3 ', Rev '0132', Slot A
Expanders on channel 0b:
Cannot Complete operation on channel 0b; Status Not Available.
Expanders on channel 2a:
Level 1: WWN 50050cc1047328ff, ID 12, Serial Number ' SHU0971734NM9N0', Product 'DS424IOM3 ', Rev '0132', Slot B
Level 2: WWN 50050cc102aa393f, ID 11, Serial Number ' SHU0954293G1B6S', Product 'DS424IOM3 ', Rev '0132', Slot B
Level 3: WWN 50050cc10312bdbf, ID 10, Serial Number ' SHU0954293G1FHG', Product 'DS424IOM3 ', Rev '0132', Slot B
Expanders on channel 2b:
Cannot Complete operation on channel 2b; Status Not Available.
Expanders on channel 2c:
Level 1: WWN 50050cc1026e773f, ID 1, Serial Number ' SHU0954293H17T6', Product 'DS424IOM3 ', Rev '0132', Slot B
Level 2: WWN 50050cc1031239ff, ID 0, Serial Number ' SHU0954293G1F8R', Product 'DS424IOM3 ', Rev '0132', Slot B
Expanders on channel 2d:
Level 1: WWN 50050cc10312b83f, ID 10, Serial Number ' SHU0954293G1FHG', Product 'DS424IOM3 ', Rev '0132', Slot A
Level 2: WWN 50050cc102aa793f, ID 11, Serial Number ' SHU0954293G1B6S', Product 'DS424IOM3 ', Rev '0132', Slot A
Level 3: WWN 50050cc10473347f, ID 12, Serial Number ' SHU0971734NM9N0', Product 'DS424IOM3 ', Rev '0132', S
so what is it?
why does fcamin device_map show blank?
chute
So I am going to say that the new one is most likely....
I think it's that one because the other loops only have 2 shelves. So before you probably had 4 shelves total and now you have 5 total. Yes/No?
Now run a 'disk show -n' to see if there are any unowned disks.
Also provide the results of 'disk show -v'
fcadmin shows blank because you don't have any of those shelves installed. You can ignore that it's blank. Its not an issue.
TDUBB1234
how can you tell that is where the new shelf is?
disk show -n shows nothing.
disk show -v
eq-ntap1> disk show -v
DISK OWNER POOL SERIAL NUMBER HOME
chute
How many shelves did you have prior to this event?
How many shelves are you attempting to add?
I can use that information with the results from below to answer your question. "how can you tell that is where the new shelf is?"
Enter privileged mode and issue the commands.
priv set advanced
disk show -n
disk show -v
TDUBB1234
I dont remember how many shelves we have. I know we added one shelf.
eq-ntap1*> disk show -n
disk show: No disks match option -n.
eq-ntap1*> disk show -v
2c.01.10     eq-ntap2  (1573890111)    Pool0  WD-WCAW30799754       eq-ntap2  (1573890111)
2c.01.3      eq-ntap2  (1573890111)    Pool0  WD-WCAW30816240       eq-ntap2  (1573890111)
2c.01.2      eq-ntap2  (1573890111)    Pool0  WD-WCAW30837917       eq-ntap2  (1573890111)
0a.00.0      eq-ntap1  (1573890252)    Pool0  HZ0AEELL              eq-ntap1  (1573890252)
2d.11.15     eq-ntap2  (1573890111)    Pool0  WD-WMATV8739175       eq-ntap2  (1573890111)
0a.00.4      eq-ntap1  (1573890252)    Pool0  HZ0JZEVL              eq-ntap1  (1573890252)
0a.00.2      eq-ntap1  (1573890252)    Pool0  HZ0JXYWL              eq-ntap1  (1573890252)
0a.00.11     eq-ntap1  (1573890252)    Pool0  HZ0JZ5GL              eq-ntap1  (1573890252)
2d.11.21     eq-ntap2  (1573890111)    Pool0  WD-WMATV8706905       eq-ntap2  (1573890111)
0a.00.21     eq-ntap1  (1573890252)    Pool0  HZ0KLGYL              eq-ntap1  (1573890252)
2d.11.11     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738693       eq-ntap2  (1573890111)
2d.11.17     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738559       eq-ntap2  (1573890111)
2d.10.2      eq-ntap2  (1573890111)    Pool0  HZ0P2RZL              eq-ntap2  (1573890111)
2d.11.20     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738298       eq-ntap2  (1573890111)
2c.01.4      eq-ntap2  (1573890111)    Pool0  WD-WCAW30939247       eq-ntap2  (1573890111)
2d.11.0      eq-ntap2  (1573890111)    Pool0  WD-WMATV8784580       eq-ntap2  (1573890111)
2c.01.0      eq-ntap2  (1573890111)    Pool0  WD-WCAW30938573       eq-ntap2  (1573890111)
2c.01.6      eq-ntap2  (1573890111)    Pool0  WD-WCAW30802832       eq-ntap2  (1573890111)
2c.01.7      eq-ntap2  (1573890111)    Pool0  WD-WCAW30832885       eq-ntap2  (1573890111)
2c.01.11     eq-ntap2  (1573890111)    Pool0  WD-WCAW30831082       eq-ntap2  (1573890111)
2c.01.1      eq-ntap2  (1573890111)    Pool0  WD-WCAW30829619       eq-ntap2  (1573890111)
2c.01.8      eq-ntap2  (1573890111)    Pool0  WD-WCAW30939548       eq-ntap2  (1573890111)
2c.01.9      eq-ntap2  (1573890111)    Pool0  WD-WCAW30814902       eq-ntap2  (1573890111)
2c.01.5      eq-ntap2  (1573890111)    Pool0  WD-WCAW30862565       eq-ntap2  (1573890111)
2d.11.10     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738323       eq-ntap2  (1573890111)
0a.00.1      eq-ntap1  (1573890252)    Pool0  HZ0K9D3L              eq-ntap1  (1573890252)
0a.00.23     eq-ntap1  (1573890252)    Pool0  HZ0JZXRL              eq-ntap1  (1573890252)
2d.11.3      eq-ntap2  (1573890111)    Pool0  WD-WMATV8738811       eq-ntap2  (1573890111)
2d.11.9      eq-ntap2  (1573890111)    Pool0  WD-WMATV8739282       eq-ntap2  (1573890111)
2d.11.19     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738821       eq-ntap2  (1573890111)
2d.11.4      eq-ntap2  (1573890111)    Pool0  WD-WMATV8779682       eq-ntap2  (1573890111)
0a.00.3      eq-ntap1  (1573890252)    Pool0  HZ0KLHYL              eq-ntap1  (1573890252)
0a.00.5      eq-ntap1  (1573890252)    Pool0  HZ0KW7KL              eq-ntap1  (1573890252)
2d.11.2      eq-ntap2  (1573890111)    Pool0  WD-WMATV8737879       eq-ntap2  (1573890111)
2d.11.7      eq-ntap2  (1573890111)    Pool0  WD-WMATV8738576       eq-ntap2  (1573890111)
0a.00.15     eq-ntap1  (1573890252)    Pool0  HZ0JLRTL              eq-ntap1  (1573890252)
0a.00.13     eq-ntap1  (1573890252)    Pool0  HZ0KLJPL              eq-ntap1  (1573890252)
2d.11.8      eq-ntap2  (1573890111)    Pool0  WD-WMATV8784808       eq-ntap2  (1573890111)
2d.11.14     eq-ntap2  (1573890111)    Pool0  WD-WMATV8735039       eq-ntap2  (1573890111)
0a.00.6      eq-ntap1  (1573890252)    Pool0  HZ0KLMWL              eq-ntap1  (1573890252)
0a.00.12     eq-ntap1  (1573890252)    Pool0  HZ0JYEZL              eq-ntap1  (1573890252)
2d.11.6      eq-ntap2  (1573890111)    Pool0  WD-WMATV8738248       eq-ntap2  (1573890111)
0a.00.16     eq-ntap1  (1573890252)    Pool0  HZ0KW8TL              eq-ntap1  (1573890252)
2d.10.7      eq-ntap2  (1573890111)    Pool0  HZ0MG1DL              eq-ntap2  (1573890111)
0a.00.19     eq-ntap1  (1573890252)    Pool0  HZ0JJUDL              eq-ntap1  (1573890252)
2d.11.1      eq-ntap2  (1573890111)    Pool0  WD-WMATV8739375       eq-ntap2  (1573890111)
2d.11.5      eq-ntap2  (1573890111)    Pool0  WD-WMATV8735936       eq-ntap2  (1573890111)
2d.11.12     eq-ntap2  (1573890111)    Pool0  WD-WMATV8779507       eq-ntap2  (1573890111)
0a.00.9      eq-ntap1  (1573890252)    Pool0  HZ0KW5PL              eq-ntap1  (1573890252)
0a.00.8      eq-ntap1  (1573890252)    Pool0  HZ0K9D2L              eq-ntap1  (1573890252)
0a.00.17     eq-ntap1  (1573890252)    Pool0  HZ0KLNRL              eq-ntap1  (1573890252)
0a.00.14     eq-ntap1  (1573890252)    Pool0  HZ0KLMAL              eq-ntap1  (1573890252)
2d.11.13     eq-ntap2  (1573890111)    Pool0  WD-WMATV8739276       eq-ntap2  (1573890111)
2d.11.16     eq-ntap2  (1573890111)    Pool0  WD-WMATV8739248       eq-ntap2  (1573890111)
0a.00.10     eq-ntap1  (1573890252)    Pool0  HZ0KW84L              eq-ntap1  (1573890252)
2d.10.12     eq-ntap2  (1573890111)    Pool0  HZ0KV9BL              eq-ntap2  (1573890111)
2d.10.8      eq-ntap2  (1573890111)    Pool0  HZ0MG2JL              eq-ntap2  (1573890111)
2d.10.18     eq-ntap2  (1573890111)    Pool0  HZ0MGARL              eq-ntap2  (1573890111)
2d.10.15     eq-ntap2  (1573890111)    Pool0  HZ0MG52L              eq-ntap2  (1573890111)
2d.10.4      eq-ntap2  (1573890111)    Pool0  HZ0LZZZL              eq-ntap2  (1573890111)
2d.10.22     eq-ntap2  (1573890111)    Pool0  HZ0JDERL              eq-ntap2  (1573890111)
0a.00.7      eq-ntap1  (1573890252)    Pool0  HZ0JMKWL              eq-ntap1  (1573890252)
0a.00.20     eq-ntap1  (1573890252)    Pool0  HZ0KLJGL              eq-ntap1  (1573890252)
0a.00.18     eq-ntap1  (1573890252)    Pool0  HZ0KLPXL              eq-ntap1  (1573890252)
2d.11.23     eq-ntap2  (1573890111)    Pool0  WD-WMATV8738322       eq-ntap2  (1573890111)
0a.00.22     eq-ntap1  (1573890252)    Pool0  HZ0KLYML              eq-ntap1  (1573890252)
2d.11.18     eq-ntap2  (1573890111)    Pool0  WD-WMATV8739690       eq-ntap2  (1573890111)
2d.10.17     eq-ntap2  (1573890111)    Pool0  HZ0JDR7L              eq-ntap2  (1573890111)
2d.10.0      eq-ntap2  (1573890111)    Pool0  HZ0KHHKL              eq-ntap2  (1573890111)
2d.10.10     eq-ntap2  (1573890111)    Pool0  HZ0LYYRL              eq-ntap2  (1573890111)
2d.10.1      eq-ntap2  (1573890111)    Pool0  HZ0LYNLL              eq-ntap2  (1573890111)
2d.10.11     eq-ntap2  (1573890111)    Pool0  HZ0M8WDL              eq-ntap2  (1573890111)
2d.10.23     eq-ntap2  (1573890111)    Pool0  HZ0MG98L              eq-ntap2  (1573890111)
2d.10.19     eq-ntap2  (1573890111)    Pool0  HZ0M7UEL              eq-ntap2  (1573890111)
2d.10.20     eq-ntap2  (1573890111)    Pool0  HZ0LYV1L              eq-ntap2  (1573890111)
2d.10.5      eq-ntap2  (1573890111)    Pool0  HZ0LZ5JL              eq-ntap2  (1573890111)
2d.10.9      eq-ntap2  (1573890111)    Pool0  HZ0M7XKL              eq-ntap2  (1573890111)
2d.10.16     eq-ntap2  (1573890111)    Pool0  HZ0M8VTL              eq-ntap2  (1573890111)
2d.10.14     eq-ntap2  (1573890111)    Pool0  HZ0KGTZL              eq-ntap2  (1573890111)
2d.10.3      eq-ntap2  (1573890111)    Pool0  HZ0LYJHL              eq-ntap2  (1573890111)
2d.10.13     eq-ntap2  (1573890111)    Pool0  HZ0KNWXL              eq-ntap2  (1573890111)
2d.10.6      eq-ntap2  (1573890111)    Pool0  HZ0M8WJL              eq-ntap2  (1573890111)
2d.10.21     eq-ntap2  (1573890111)    Pool0  HZ0M87TL              eq-ntap2  (1573890111)
2d.11.22     eq-ntap2  (1573890111)    Pool0  WD-WMATV8739176       eq-ntap2  (1573890111)
2a.12.16     eq-ntap2  (1573890111)    Pool0  N0337X8L              eq-ntap2  (1573890111)
2a.12.3      eq-ntap2  (1573890111)    Pool0  N033EL4L              eq-ntap2  (1573890111)
2a.12.21     eq-ntap2  (1573890111)    Pool0  N033JD6L              eq-ntap2  (1573890111)
2a.12.15     eq-ntap2  (1573890111)    Pool0  N033GGTL              eq-ntap2  (1573890111)
2a.12.8      eq-ntap2  (1573890111)    Pool0  N033L0PL              eq-ntap2  (1573890111)
2a.12.14     eq-ntap2  (1573890111)    Pool0  N033EKXL              eq-ntap2  (1573890111)
2a.12.18     eq-ntap2  (1573890111)    Pool0  N033JKKL              eq-ntap2  (1573890111)
2a.12.6      eq-ntap2  (1573890111)    Pool0  N033670L              eq-ntap2  (1573890111)
2a.12.5      eq-ntap2  (1573890111)    Pool0  N033JBGL              eq-ntap2  (1573890111)
2a.12.9      eq-ntap2  (1573890111)    Pool0  N0337WSL              eq-ntap2  (1573890111)
2a.12.17     eq-ntap2  (1573890111)    Pool0  N0337XDL              eq-ntap2  (1573890111)
2a.12.0      eq-ntap2  (1573890111)    Pool0  N033M0SL              eq-ntap2  (1573890111)
2a.12.4      eq-ntap2  (1573890111)    Pool0  N033LM0L              eq-ntap2  (1573890111)
2a.12.22     eq-ntap2  (1573890111)    Pool0  N033L0BL              eq-ntap2  (1573890111)
2a.12.7      eq-ntap2  (1573890111)    Pool0  N033EP4L              eq-ntap2  (1573890111)
2a.12.13     eq-ntap2  (1573890111)    Pool0  N033ER8L              eq-ntap2  (1573890111)
2a.12.1      eq-ntap2  (1573890111)    Pool0  N033JRUL              eq-ntap2  (1573890111)
2a.12.19     eq-ntap2  (1573890111)    Pool0  N02ZUP4L              eq-ntap2  (1573890111)
2a.12.10     eq-ntap2  (1573890111)    Pool0  N033GXLL              eq-ntap2  (1573890111)
2a.12.2      eq-ntap2  (1573890111)    Pool0  N0337WWL              eq-ntap2  (1573890111)
2a.12.20     eq-ntap2  (1573890111)    Pool0  N0334EDL              eq-ntap2  (1573890111)
2a.12.23     eq-ntap2  (1573890111)    Pool0  N0337R4L              eq-ntap2  (1573890111)
2a.12.11     eq-ntap2  (1573890111)    Pool0  N0336BUL              eq-ntap2  (1573890111)
2a.12.12     eq-ntap2  (1573890111)    Pool0  N033LZKL              eq-ntap2  (1573890111)
chute
Ok I did some digging and found out that you have everything configured correctly. Great job! Here is the simplest way to explain what I did. If this is something you need to do again in the future, just compare old asup's to new one's with the info below and it will tell you exactly what you need. Bottom line, eq-ntap2 has all of your spares and you can start adding to your aggregates from that pool of disks.
Looked at an old autosupport and compared it with a new one.....
sysconfig -a
sysconfig -r
I was correct in my assumption about the shelf I called out above. You will notice it's not on the old asup.
New shelf:::
Level  3: WWN 50050cc10312b83f, ID 10, Serial Number ' SHU0954293G1FHG', Product 'DS424IOM3       ', Rev '0132', Slot A
Level  3: WWN 50050cc1047328ff, ID 12, Serial Number ' SHU0971734NM9N0', Product 'DS424IOM3       ', Rev '0132', Slot B
Then, just take a look at home many more spares you now have in the new config. You will notice there are exactly 24 more.
OLD:::
EQ-NTAP2
sysconfig -r
Pool0 spare disks
RAID Disk Device   HA  SHELF BAY CHAN Pool Type  RPM  Used (MB/blks)    Phys (MB/blks)
Spare disks for block or zoned checksum traditional volumes or aggregates
spare    2a.11.0  2a    11  0   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816 (not zeroed)
spare    2a.11.1  2a    11  1   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816 (not zeroed)
spare    2a.11.2  2a    11  2   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816 (not zeroed)
spare    2a.11.6  2a    11  6   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.11.9  2a    11  9   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.11.10 2a    11  10  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
NEW:::
EQ-NTAP2
sysconfig -r
Pool0 spare disks
spare    2a.12.0  2a    12  0   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.1  2a    12  1   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.2  2a    12  2   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.3  2a    12  3   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.4  2a    12  4   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.5  2a    12  5   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.6  2a    12  6   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.7  2a    12  7   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.8  2a    12  8   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.9  2a    12  9   SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.10 2a    12  10  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.11 2a    12  11  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.12 2a    12  12  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.13 2a    12  13  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.14 2a    12  14  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.15 2a    12  15  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.16 2a    12  16  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.17 2a    12  17  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.18 2a    12  18  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.19 2a    12  19  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.20 2a    12  20  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.21 2a    12  21  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.22 2a    12  22  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2a.12.23 2a    12  23  SA:A   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2d.11.0  2d    11  0   SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816 (zeroing, 7% done)
spare    2d.11.1  2d    11  1   SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816 (zeroing, 7% done)
spare    2d.11.2  2d    11  2   SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816 (zeroing, 7% done)
spare    2d.11.6  2d    11  6   SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2d.11.9  2d    11  9   SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816
spare    2d.11.10 2d    11  10  SA:B   0  BSAS  7200 847555/1735794176 847884/1736466816
Hope this helps.
chute
ryanbeaty
Can you give us specs on your NetApp?
Model
ONTAP Version
The DS42xx and DS14MK2 aren't supported with everything.
Did you get confirmation that you are running a compatible configuraiton? WHen you add just one link from the NetApp to these shelves your NetApp should see the disks (disk show -n) <-- Non owned disks.
If you aren't seeing disks that means something is not either cabled right, or it isn't a supported config.
Run Config Advisor to check your cabling.