FAS2050 - QLE2464 - System not recognizing QLE2464 (4-Port) FC Card in expansion PCI-E slot.
dkkelly
Hardware: FAS2050 - Dual controllers
ONTAP:     7.3.3
System has working QLE2462 (2-port) FC card in expansion PCI-E slot. No issues. Tried upgrading the card to the QLE2464 (4-port) system does not recognize it. Card lights up, that's about it.
Iadfas02: cf takeover
Pulled iadfas01 controller. Installed new 4 port card. Reinstalled controller.
Iadfas02: cf giveback
At this point the system did not recognize the new card. Decided to investigate further and roll back to the original configuration for the time being.
Pulled iadfas01 controller. Installed 2 port card. Reinstalled controller.
See attached...
Any thoughts?
10 REPLIES 10
scottgelb
What is the NetApp part number?   For the 2050, the X2054A-R6 (Qlogic 2432) is the supported quad card initiator.  The quad port target HBA is X1130A-R6... but looks like an initiator and the 2054a is the 2432 not 2464 on parts finder.
aborzenkov
Please show “sysconfig -ca” output on this system.
cedric_renauld
Or the messages to see the Boot messages
dkkelly
Please note that the system now has the original QLE2432 PCI-E expansion HBA installed.
iadfas01> sysconfig -c
sysconfig: There are no configuration errors.
iadfas01> sysconfig -a
        NetApp Release 7.3.3: Thu Mar 11 22:43:52 PST 2010
        System ID:  (iadfas01); partner ID: 0135031487 (iadfas02)
        System Serial Number:  (iadfas01)
        System Rev: G1
        System Storage Configuration: Mixed-Path HA
        System ACP Connectivity: NA
        slot 0: System Board 2198 MHz (System Board XIV H1)
                Model Name:         FAS2050
                Part Number:        110-00048
                Revision:           H1
                Serial Number:      813698
                BIOS version:       3.0
                Processors:         1
                Processor ID:       0xf29
                Microcode Version:  0x2f
                Memory Size:        2048 MB
                NVMEM Size:         256 MB of Main Memory Used
                CMOS RAM Status:    OK
                Controller:         A
        slot 0: Dual 10/100/1000 Ethernet Controller G20
                e0a MAC Address:    00:a0:98:0c:6a:5c (auto-1000t-fd-up)
                e0b MAC Address:    00:a0:98:0c:6a:5d (auto-1000t-fd-up)
                Device Type:        Rev 6
                        memory mapped I/O base 0xd9600000, size 0x20000
                        memory mapped I/O base 0xd9620000, size 0x20000
                        I/O base 0x0000cfe0, size 0x20
                        memory mapped I/O base 0xd9640000, size 0x20000
                        memory mapped I/O base 0xd9660000, size 0x20000
                        I/O base 0x0000cfc0, size 0x20
                        memory mapped I/O base 0xd8000000, size 0x1000
                        I/O base 0x0000ffe0, size 0x20
        slot 0: Interconnect HBA:   Mellanox IB MT25204
                GUID: 0x2c90281369800   LID: 0x2a82     Remote LID: 0x2abf
                Firmware rev:           1.0.800
                Hardware rev:           160
                Command rev:            1
                        memory mapped I/O base 0xd9000000, size 0x100000
                        prefetchable memory base 0xdb800000, size 0x800000
        slot 0: Fibre Channel Target Host Adapter 0a
                (Dual-channel, QLogic 2432(2462) rev. 2, 64-bit, <ONLINE>)
                Firmware rev:     4.5.2
                Host Port Addr:   bc2700
                Cacheline size:   16
                SRAM parity:      Yes
                FC Nodename:      50:0a:09:80:88:7c:6a:82 (500a0980887c6a82)
                FC Portname:      50:0a:09:81:98:7c:6a:82 (500a0981987c6a82)
                Connection:       PTP, Fabric
                SFP Vendor Name:  FINISAR CORP.
                SFP Vendor P/N:   FTLF8524P2BNV
                SFP Vendor Rev:   A
                SFP Serial No.:   PD73687
                SFP Connector:    LC
                SFP Capabilities: 1, 2, 4 Gbit/Sec
                        I/O base 0x0000ee00, size 0x100
                        memory mapped I/O base 0xd9200000, size 0x4000
        slot 0: FC Host Adapter 0b (QLogic 2432 rev. 2, L-port, <UP>)
                Firmware rev:      4.5.2
                Host Loop Id:      7
                FC Node Name:      5:00a:098100:027c58
                SFP Vendor:        FINISAR CORP.
                SFP Part Number:   FTLF8524P2BNV
                SFP Serial Number: PD70H85
                SFP Capabilities:  1, 2 or 4 Gbit
                Link Data Rate:    2 Gbit
                 16  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7VD)
                 17  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7WU)
                 18  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7WM)
                 19  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7TF)
                 20  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7WC)
                 21  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7MF)
                 22  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7UT)
                 23  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7T3)
                 24  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7TC)
                 25  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7NP)
                 26  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7V2)
                 27  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7YG)
                 28  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A805)
                 29  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A7YA)
                 32  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S51)
                 33  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SHL)
                 34  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SJK)
                 35  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S4W)
                 36  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S9R)
                 37  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S4M)
                 38  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S75)
                 39  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309S8T)
                 40  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SJ4)
                 41  : NETAPP   X276_S10K7288F10 NA07 272.0GB 520B/sect (3KR1YWRT00009712PAUE)
                 42  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SHS)
                 43  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SJ5)
                 44  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SJ3)
                 45  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309SJF)
                 48  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8FT)
                 49  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8EW)
                 50  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309V10)
                 51  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8FM)
                 52  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8F6)
                 53  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8FL)
                 54  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A3WH)
                 55  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8F0)
                 56  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309YU0)
                 57  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A3W8)
                 58  : NETAPP   X276_S10K7288F10 NA07 272.0GB 520B/sect (3KR3HG2900009728VD70)
                 59  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P840AWS3)
                 60  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P8309YU5)
                 61  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P830A8HC)
                 64  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EUTN)
                 65  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EUUS)
                 66  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EUU5)
                 67  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EUUT)
                 68  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EUU4)
                 69  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P850C7VR)
                 70  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P880EV8W)
                 71  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F6HG)
                 72  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F85V)
                 73  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F5SG)
                 74  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F84A)
                 75  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F6K1)
                 76  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F84K)
                 77  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890F5LK)
                 80  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVE8)
                 81  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FV8K)
                 82  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVDS)
                 83  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FUHF)
                 84  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FUT6)
                 85  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVD4)
                 86  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVD6)
                 87  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVD1)
                 88  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FUJL)
                 89  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVD5)
                 90  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVDJ)
                 91  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FUG4)
                 92  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FUAP)
                 93  : NETAPP   X276_FAL9E288F10 NA05 272.0GB 520B/sect (DH07P890FVDE)
                Shelf 1: ESH4  Firmware rev. ESH A: 14  ESH B: 14
                Shelf 2: ESH4  Firmware rev. ESH A: 14  ESH B: 14
                Shelf 3: ESH4  Firmware rev. ESH A: 14  ESH B: 14
                Shelf 4: ESH4  Firmware rev. ESH A: 14  ESH B: 14
                Shelf 5: ESH4  Firmware rev. ESH A: 14  ESH B: 14
                        I/O base 0x0000ef00, size 0x100
                        memory mapped I/O base 0xd9204000, size 0x4000
        slot 0: SAS Host Adapter 0c (LSI Logic 1068E rev. B2, SAS, <UP>)
                Firmware rev:      1.26.03.00
                Base WWN:          f:080c6a:8200000:00
                Phy State:         [0] Enabled, 3.0 Gb/s
                                   [1] Enabled, 3.0 Gb/s
                                   [2] Enabled, 3.0 Gb/s
                                   [3] Enabled, 3.0 Gb/s
                00.0 : NETAPP   X283_HGEMIT75SSS AA2A 635.5GB 512B/sect (P8GZ8NGF)
                00.1 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YZFY)
                00.2 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24L1F)
                00.3 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24L0N)
                00.4 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24L2C)
                00.5 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YXPJ)
                00.6 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24MFF)
                00.7 : NETAPP   X298_HSATE01TSSS A38G 847.5GB 512B/sect (MQ0L7NDF)
                00.8 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24MD1)
                00.9 : NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YZ09)
                00.10: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YZ3T)
                00.11: NETAPP   X298_SMUSK01TSSS NA00 847.5GB 512B/sect (9WK1XXQ9)
                00.12: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YZ1X)
                00.13: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24KWE)
                00.14: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24KXT)
                00.15: WDC      WD1003FBYX-05YSS NA00 847.5GB 512B/sect (WD-WCAW32199606)
                00.16: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD0YXF8)
                00.17: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD24KT2)
                00.18: NETAPP   X283_SGLXY750SSS APPZ 635.5GB 512B/sect (5QD21DWY)
                00.19: NETAPP   X283_HGEMIT75SSS AA2A 635.5GB 512B/sect (P8GZGM6F)
                Shelf   0: ESAS  Firmware rev. SAS A: 05 SAS B: 05
                        I/O base 0x0000df00, size 0x100
                        memory mapped I/O base 0xd9410000, size 0x4000
                        memory mapped I/O base 0xd9400000, size 0x10000
        slot 0: ATA/IDE Adapter 0e (0x000001f0)
                0e.0                 STEC     NACF256MM1U-B11 01/17/07 245MB 512B/sect (STI1M93508050154714)
                        I/O base 0x0000ffc0, size 0x8
                        I/O base 0x0000ffb8, size 0x4
                        I/O base 0x0000ffc8, size 0x8
                        I/O base 0x0000ffbc, size 0x4
                        I/O base 0x0000ffd0, size 0x10
                        memory mapped I/O base 0xd8001000, size 0x400
        slot 1: FC Host Adapter 1a (QLogic 2432 rev. 3, N-port, <UP>)
                Board name:        QLE2462
                Serial Number:     RFC0802K08614
                Firmware rev:      4.5.2
                Host Port Id:      0xbc0a00
                FC Node Name:      2:100:001b32:0fe663
                SFF Vendor:        FINISAR CORP.
                SFF Part Number:   FTLF8524E2KNL
                SFF Serial Number: PCR19JB
                SFF Capabilities:  1, 2 or 4 Gbit
                Link Data Rate:    4 Gbit
                Switch Port:       fsw01.hhc:1-15
                fsw01.hhc:1-2.126 Tape:  HP      Ultrium 4-SCSI   H5AS (HU18101HDE)
                fsw01.hhc:1-4.126 Tape:  HP      Ultrium 4-SCSI   H5AS (MXP104179H)
                fsw01.hhc:1-5.126 Tape:  HP      Ultrium 4-SCSI   H5AS (MXP1109ABJ)
                fsw01.hhc:1-6.126 Tape:  HP      Ultrium 4-SCSI   H5AS (HU1037CC66)
                fsw01.hhc:1-3.126 Tape:  HP      Ultrium 4-SCSI   H5AS (HU17350AAV)
                        I/O base 0x0000be00, size 0x100
                        memory mapped I/O base 0xd9800000, size 0x4000
        slot 1: FC Host Adapter 1b (QLogic 2432 rev. 3, L-port, <UP>)
                Board name:        QLE2462
                Firmware rev:      4.5.2
                Host Loop Id:      7
                FC Node Name:      2:101:001b32:2fe663
                SFF Serial Number: PCR1A10
                        I/O base 0x0000bf00, size 0x100
                        memory mapped I/O base 0xd9804000, size 0x4000
        Baseboard Management Controller:
                Firmware Version:   1.2
                IPMI version:       2.0
                DHCP:               off
                BMC MAC address:
                IP address:
                IP mask:
                Gateway IP address:
                BMC ARP interval:   10 seconds
                BMC has (1) user:   naroot
                ASUP enabled:       on
                ASUP mailhost:
                ASUP from:
                ASUP recipients:
                Uptime:             0 Days, 21:39:33
iadfas01>
aborzenkov
Providing output of different command in wrong time is not going to help ☺ Next time if you try to add this adapter again please provide output of exactly the command I asked you.
dkkelly
iadfas01> sysconfig -ca
sysconfig: slot 1 OK: X2055A: QLogic ISP 2432; PCI-E dual-port Fibre Channel (QLE2462)
sysconfig: System configuration meets block protocol requirements.
iadfas01>
scottgelb
-ca is a very useful command. It parses /etc/sysconfigtab to get a part number from the card description string. And also if unsupported or not for the platform. It likely would say unsupported card if you still had it installed. The QLogic part number is different on the netapp 2054a which isn't what you had
AGUMADAVALLI
according to the Netapp hardware universe, the mentioned quad port card doesn't support on this filer. Please check with "https://hwu.netapp.com/Adapter/Index"
thank you,
AK G
dkkelly
The following supported adapters listed appear* to be the same card i'm working with. Is this just a matter of the configuration of the card that makes it a target or initiator?
X1130A-R6
X2054A-R6
X1130A-R6
Is this the same card that NetApp has re-branded or do I have a different HBA that will not work?
Thanks
scottgelb
The NetApp supplied card is x2054a is initiator mode only... not sure if a jumper on the card or an ONTAP driver forcing it but doesn't support target connections.  The new 8GB FC cards support either target or initiator like the onboard ports using fcadmin config...but these adapters are initiator only.  If you are not using the NetApp supplied card then not sure how to tell but you might be able to find a netapp card and compare everything is exact...just unsupported probably if not netapp supplied.