ONTAP Discussions
Snapmirror running slow - 2MB/s over 10GbE
ed_symanzik
I am seeing unhealthy snapmirror times; transfer rates on the order of 2MB/s over 10GbE.
last-transfer-size     last-transfer-duration
      631.6GB            86:35:23
      11.16GB            2:12:48
      755.5GB            91:32:48
Schedule is to run every 10 minutes.
The network is clean.  ifstat has not recorded an error in months.
No duplex mismatches and negotiated speed is 10000.
Network is not maxed out, hits 80% at times.
Jumbo frames are enabled throughout.
CPU load is low on a pair of FAS6220's.
Systems using the storage get good performance.
Throttle is unlimited.
What else do I check?
30 REPLIES 30
DOMINIC_WYSS
are you using jumbo frames everywhere or just on the snapmirror interfaces? make sure every switch between the source and destination filer is configured correctly for jumbo frames.
which size are the jumbo frames? if the switches and Ontap are configured to 9000 and you are using vlans, then either  set the switches bigger or Ontap smaller.
check your routing table (route -s). if you have e0M on the same subnet as another interface, then sometimes the default gateway routing goes over it (and that's 100Mbit!). then you need to redesign your network config...
ed_symanzik
Jumbo frames everywhere.  VLAN'd correctly.  Ontap configured to 9000 mtu and the switches to something larger (9018, I think).
We did find an odd route and removed it. Switch statistics showed that it wasn't being used though the the situation has not improved (up to 7 days on the current snapshot).
aborzenkov
What is latency between sites?
ed_symanzik
64 bytes from 172.16.20.33: icmp_seq=1 ttl=64 time=0.196 ms
In getting this number I did discover that the NetApp ping has packet-size and disallow-fragmentation options.
na-adm::> net ping -node na-adm-01 -destination 172.16.34.9 -disallow-fragmentation true -packet-size 2000 -record-route -show-detail -verbose
  (network ping)
ping: sendto: Message too long
Double-checked with our Network Team and jumbo frames are set.  Double-checked the NetApp and jumbo frames are set on the physical ports, the ifgrp, and the vlan.
DOMINIC_WYSS
just to be sure I would temporarely set the MTU to standard 1500 (just on source and destination filers).
we had a customer with jumbo frames problems on 10GbE and it was an issue on the switches. they just couldn't handle jumbos correctly with 10GbE.
another thing may be flowcontrol, we always disable it on 10GbE: ifconfig eXa flowcontrol none. I've seen it at some customers that Netapp Professional Services also disables it on all 10GbE interfaces.
JGPSHNTAP
I echo the above... I've also seen instances where a snapmirror appears "stuck"   When everything checks out and the configurations are correct, I've had to abort the snapmirror and start it over and everything worked fine.
ed_symanzik
Can flow control and the MTU be changed without disruption?
With what switches did you see the jumbo/10GbE issue?
DOMINIC_WYSS
MTU change is realtime without any disruption.
disabling flowcontrol will do a port down/up with a minimal disruption of a few seconds if you don't have an ifgrp with two ports. you could do a LIF migrate to the other node and back again.
we had the issue with Brocade ICX switches.
ed_symanzik
I was able to do the lif migration, but I cannot change the flowcontrol setting:
na-adm::> network interface migrate-all -node na-adm-02
na-adm::> network port modify -node na-adm-02 -port a0a-1634 -flowcontrol-admin none
Warning: Changing the network port settings will cause a several second interruption in carrier.
Do you want to continue?
{y|n}: y
Error: command failed: Can't change autoneg, speed or duplex for a vlan.
na-adm::> network port modify -node na-adm-02 -port a0a -flowcontrol-admin none
Do you want to continue? {y|n}
: y
Error: command failed: Can't change autoneg, speed or duplex for an ifgrp.
na-adm::> network port modify -node na-adm-02 -port e3b -flowcontrol-admin none
{y|n}
: y
Error: command failed: Set media options failed.
NetApp_SEAL
Right - you can't change Flow Control at the VLAN or ifgrp level, and you cannot modify Flow Control on a port that's part of an ifgrp or has tagged VLANs hanging off of it.
By migrating the LIFs away from the node that you want to make the changes on, it should afford you the ability to completely rebuild the ifgrp, which is what you would have to do in this case in order to change the Flow Control settings on the ports that make up the ifgrp.
Breaking / rebuilding the the ifgrp on the node after performing a LIF migration to the other node would be no different than when you reboot the node during an NDO upgrade, etc...
ed_symanzik
Is it possible to remove a port from the lif, change flow control, and re-add the port to the lif?
NetApp_SEAL
Yes. As long as there are no LIFs on any of the ports belonging to the ifgrp, then you should be able to change the flow control setting on the ports themselves.
Just did this in my lab.
ed_symanzik
So, this was my plan.
network port ifgrp remove-port -node na-adm-02 -ifgrp a0a -port e3b
network port ifgrp add-port -node na-adm-02 -ifgrp a0a -port e3b
network port ifgrp remove-port -node na-adm-02 -ifgrp a0a -port e0d
network port modify -node na-adm-02 -port e0d -flowcontrol-admin none
network port ifgrp add-port -node na-adm-02 -ifgrp a0a -port e0d
net int revert -lif *
Trouble is, the intercluster lif uses a vlan port that sits on a0a and intercluster lifs won't migrate to another node.
na-adm::> network int modify -vserver na-adm-02 -lif ic_lif0 -failover-group fg-a0a-1634
  Error: command failed: Failover group fg-a0a-1634 cannot be used because it
       contains ports on a remote node.
na-adm::> network port ifgrp remove-port -node na-adm-02 -ifgrp a0a -port e3b
  Error: command failed: Failed to disable the ifgrp "a0a" while preparing to
       remove a port from it.
na-adm::> network interface show -vserver na-adm-02
            Logical    Status     Network            Current       Current Is
Vserver     Interface  Admin/Oper Address/Mask       Node          Port    Home
na-adm-02
            clus1        up/up    169.254.98.142/16  na-adm-02     e0c     true
            clus2        up/up    169.254.74.124/16  na-adm-02     e0e     true
            ic_lif0       up/up    172.16.34.8/24        na-adm-02     a0a-1634                <==========
        true
            mgmt1        up/up    35.8.5.34/26       na-adm-02     e0M     true
4 entries were displayed.
Everything else migrated to the other node.
So, do I have things misconfigured?  or am I missing a step?
ed_symanzik
Okay.  I found a NetApp engineer who told me
It looks like you are using our UTA card (either X1139 or X1140).  Unfortunately, with that particular adapter, you cannot disable flow control on the storage side.  This has been fixed with the X1143 UTA2.  UTA2s are now onboard on the FAS8000s and FAS2500s.
With the UTA, if flow control is disabled on the switch side, you will not see any flow control pause frames on the network.
And flow-control has been disabled on the switch from the start so I've reached a dead end on this trail.
ed_symanzik
Set MTU to 1500.  No change in performance.
NetApp_SEAL
Question - can you post an output of the following:
- Traceroute from source to destination IC LIF
- routing-group show
- routing-group route show
I'm just curious
So I've been battling this same issue for a client for a large part of the day today.
FAS8040 at source, FAS3220 at destination. Both sites using 10 Gb interface groups for data with respective VLAN tagging. Using the same data interface group vs. a dedicated port (client doesn't have the proper SFPs for the other UTA2 ports to dedicate - maybe in the future). The client's network admin was only seeing about 1 Gb utilization over the 10 Gb link between sites. So I was like..yeah...great...I've seen this one before.
I ran into two issues:
1) Routing group configuration
2) Jumbo Frames configuration
When the node intercluster LIFs got created, it created the respective routing groups (but not routes). The VLAN isn't spanned, so I needed to create the proper routes. Did that. Can ping fine. Yay! Still had issues. So I ran a traceroute from the IC LIF on Node A at souce site to the IC LIF on Node B at the destination site. Even with the routing group (and route) in place, the first hop at each site was to the node / cluster management VLAN on the respective node (which was interesting to me since management is on 1) a different physical port and 2) a different subnet.
The route for inter-cluster was using a destination of 0.0.0.0/0 (but with the proper gateway - the SVI of the SnapMirror VLAN). Decided to delete the route and create a new one. So, I went old skool 7-Mode static route on it and set the proper destination (the subnet of the destination site) and the same gateway (the local SnapMirror VLAN SVI). Now the trace comes back clean and the first hop is the SnapMirror VLAN SVI. w00t!
Still won't work.
Turns out that there WASN'T Jumbo Frames all the way from source to destination. The topology has 5Ks at each site then two 7Ks in between the sites over to 10 Gb links. I believe the network admin forgot to set the per-VLAN MTU size for the SnapMirror VLAN on the 7Ks to 9000. I'll get him to fix that tomorrow.
So I went back and set the MTU to 1500 on the VLAN interfaces on each node. Aborted / restarted the SnapMirror relationships (they seemed hung). Now it works like a charm
Hope to have some metrics to compare against in the AM to validate.
Hope this helps. Let me know!
Cheers,
Trey
ed_symanzik
I have two nodes dual connected to the same two switches, so traceroute shows one hop.
na-adm::> net routing-groups show -vserver na-adm-*
  (network routing-groups show)
          Routing
Vserver   Group     Subnet          Role         Metric
na-adm-01
          c169.254.0.0/16
                    169.254.0.0/16  cluster           30
          i172.16.34.0/24
                    172.16.34.0/24  intercluster      40
          n35.8.5.0/26
                    35.8.5.0/26     node-mgmt         10
na-adm-02
          c169.254.0.0/16
          i172.16.34.0/24
          n35.8.5.0/26
6 entries were displayed.
na-adm::> net routing-groups route show -vserver na-adm-*
  (network routing-groups route show)
          Routing
Vserver   Group     Destination     Gateway         Metric
na-adm-01
          n35.8.5.0/26
                    0.0.0.0/0       35.8.5.1        10
na-adm-02
          n35.8.5.0/26
2 entries were displayed.
The big weirdness at this point is that outgoing jumbo pings fail but incoming jumbo pings succeed. Jumbos also work across the cluster switches.
NetApp_SEAL
Ok, so this is local Layer 2, correct? Not routing over a WAN to another site, so therefore, no routing required?
ed_symanzik
Correct.  The snapmirror is three switches away, but no router.  The jumbo ping shows up node-switch-node.
NetApp_SEAL
Have you checked the SnapMirror TCP window size?
node run -node * options snapmirror.window_size
If not set at recommended for when using 10 Gb, set value to 8388608
node run -node * options snapmirror.window_size 8388608
(Source: https://library.netapp.com/ecmdocs/ECMM1278318/html/onlinebk/protecting/task/t_oc_prot_sm-adjust-tcp-window-size.html)
Another thing I could think to check would be the ingress/egress of the ports. Perhaps some QoS policy issues at the network layer (probably unlikely but worth looking in to - I've seen cases where someone would set QoS at the switch level where bandwidth was getting choked to death for Ethernet traffic).