FAS2020 and APC UPS interaction for shutdown

JoseCasaux
6,645 Views

Hello folks, a customer is asking us if our FAS2020 can work tight with APC UPS software PowerShute, in order to configure an automated storage shutdown. If is not compatible, which UPS vendor can be recommended to do so? Thanks a lot.

1 ACCEPTED SOLUTION

scottgelb
6,601 Views

Yes the fas can shutdown from the ups timeout setting.  The faq has a link to this kb which has an example warning time at 10 minutes and critical shutdown 5 minute time.  https://kb.netapp.com/support/index?page=content&id=3010916

View solution in original post

3 REPLIES 3

scottgelb
6,634 Views

Found the FAQ after years of not seeing it... ONTAP 8.0 and earlier only and APC is supported for those older releases.  https://kb.netapp.com/support/index?page=content&id=3011918&locale=en_US

JoseCasaux
6,604 Views

Hello Scottgelb, as I understand what DataONTAP 8 and earlier can do was to shutdown the storage when it detected a low battery status of the UPS. But the question is if the FAS can follow orders from the UPS to shutdown. I don't know if it's possible.

Thank you.

scottgelb
6,602 Views

Yes the fas can shutdown from the ups timeout setting.  The faq has a link to this kb which has an example warning time at 10 minutes and critical shutdown 5 minute time.  https://kb.netapp.com/support/index?page=content&id=3010916