I know this has been asked an answered several times but I am a bit new to storage and want to know what to expect. I am following the following Netapp KB on graceful shutdown: https://kb.netapp.com/app/answers/answer_view/a_id/1003836/~/what-is-the-procedure-for-graceful-shutdown-and-power-up-of-a-storage-system
We have two 8020 controllers each controller has 2 nodes both connected to two (CN 1610) intetrcluster switches. From the KB it sounds like for 8.3.2, all I have to do is login to the SP interface on each node and run: 'halt local -inhibit-takeover true' and wait for the LOADER prompt to appear on all nodes before shutting it down. For powerup, bring up the shelves first and then the controllers. Questions:
1) Does the above sound right?
2) Do I need to shut down the CN1610 switches?
3) During powerup, do I need to login to SP and then issue a boot command at the LOADER prompt or will it just boot into Ontapp?
Are there any common mistakes that people make that I can avoid by prepping in advance?
Solved! See The Solution
@Damien_Queen wrote:
2) Disable failover (and HA if needed)
Hi Damien_Queen, with regards to #2, is that a seprate command or will the 'halt local -inhibit-takeover true' in the KB take care of that? From the power-down KB, I thought that will not necessary because even the KB warning says this will not failover and if you want it then to issue a manual command.
- If that is a separate command, will this work? "storage failover modify -enabled false -node nodename"
- To disable HA, can I use: "storage failover modify -mode non_ha -node nodename"
Should I issue both the above commands with each nodename.